Advanced Central Plant Heat Pump Modeling: Heat Pump with Booster Heater
March 6th 2026

Advanced Central Plant Heat Pump Modeling: Heat Pump with Booster Heater

With the introduction of the Central Plant Heat Pumps (CPHP) in ApacheHVAC, which can serve both the Chilled Water Loop (ChWL) and Hot Water Loop (HWL), users can now model both Air-to-Water Heat Pumps (AWHP) and Water-to-Water Heat Pumps (WWHP). Moreover, this new feature has prompted inquiries about how CPHP can be used to build a custom AWHP or WWHP system. This multi-part article will explore these custom scenarios in detail.

In the first article of this multi-part series, I will explain an approach to modeling a CPHP with a Booster (or Top-off) Heater Boiler. ApacheHVAC allows users to select from a range of heating sources, including Natural Gas Boiler, Electric Boiler, Water-to-Water Heat Pump, or Air-to-Water Heat Pump, as the booster heater source.

Figure 1: Layout of Heat Pump with Booster

System Scenario and Use Cases

Scenario 1 is that a mechanical design engineer might install a new CPHP upstream of an existing (or new) boiler to preheat water to 120°F, with the downstream boiler then heating it to 140°F.

Another scenario is that an AWHP might not supply hot water effectively at low ambient temperatures, so a backup heating source could be installed downstream of the AWHP for such conditions.

These configurations can be set up using the “Auxiliary Heat Source" option in the Hot Water Loop tab of ApacheHVAC, which adds a booster heater downstream of the CPHP to reach the desired temperature. This article explains how to configure this setup in ApacheHVAC.

Modeling Workflow in ApacheHVAC

Step 1: Define the AWHP/WWHP supply water temperature as the “Primary Supply” in the HWL.

This step defines the CPHP leaving water temperature. Referring to Figure 1, we are defining the temperature at “HWL to Booster” section.

asset_image

Figure 2: Defining AAHP Leaving Water Temperature 

Step 2: Add a Secondary Loop and check the “Enable independent secondary loop supply water temperature control" box. Referring back to Figure 1, in this step, we define the temperature of the water leaving the booster heating source, “HWL Supply.”

Step 2a: In the “Secondary Loop,” update the “Design hot water Supply Temperature” to be representative of the booster boiler leaving temperature.

asset_image

Figure 3: Defining Booster Boiler Leaving Water Temperature 

Step 3: Turn on the “Auxiliary heat source” by checking the “Downstream auxiliary heat source” box on the Auxiliary Heat Source tab. Referring back to Figure 1, in this step, we define the type and properties of the booster heater. 
 
Step 3a: Change the “Location on the hot water loop” to “Dedicated supply for selected secondary loop”
 
Step 3b: Select the Secondary loop created in step 2.
 
Step 3c: Set the “Model type” to match the booster boiler type.

Figure 4: Editing Properties of Booster Boiler

Result Visualization

We can verify the implementation of the CPHP with the Booster heater setup in IESVE through the VistaPro application, which provides visualization tools for simulation results.

The screenshot below illustrates the HWL results in VistaPro. It shows that the “Primary Supply Temperature” (HP leaving temperature) in the loop is 120 °F (as defined in Figure 2 above), while the "Auxiliary heat source leaving temperature” (Booster boiler leaving temperature) is 140 °F (as defined in Figure 3).

Figure 5: Result Visualization in VistaPro 

Conclusion

Modeling a CPHP with a booster heater in ApacheHVAC offers a simple and effective way to meet hot water temperature requirements under all conditions.

By defining the primary heat pump supply temperature, adding a controlled secondary loop, and enabling the auxiliary heat source, engineers can accurately represent both the heat pump and booster system. VistaPro results confirm how each component contributes to the final supply temperature. This hybrid approach allows the primary heat pump to operate efficiently for most of the year while relying on the booster heater only when needed, offering a cost-effective and reliable solution for buildings in colder climates or requiring higher supply temperatures.