Using its Ci2 Consulting service, IES undertook a detailed investigation of BMS data logs to uncover energy wastage and understand ‘Cause & Effect’ of different Control changes.
- High level analysis of AMR data
- Detailed investigation of BMS data logs for ‘Cause & Effect’ analysis
- Identified 24-hr chiller use in winter months due to AHU cooling coil control fault
- Opportunity to reduce energy wastage
- Minimise wasteful cooling when free cooling available
- Substantial energy savings on reduction of chiller run hours
- Poor control on chiller identified
- Compressor pulsing on/off over short time periods
- Substantially reduced lifetime on compressor if left unaddressed
- Data driven approach to maintenance, proactive (preventing failure) rather than reactive (fixing failures by replacing with new plant)