Running the Part L 2021 – England – ApacheSim method Simulation fails.

Download PDF Version of Answer

The first thing to do is select the failed task, so in this case the Notional Building, to view the error/reason for the task failing.

In this case the problem is a surface temperature instability due to a Notional Building construction (a lightweight metal clad construction used for the Warehouse activity).

The first suggestion is to reduce the simulation time step. This can be done in Set Building & System Data on the Simulation tab. The default time step is 10 minutes so reduce it to 1 minute and try running the simulation again.

If you get a different error then please take a screenshot of the error and attach this to an email to support@iesve.com